Posted By: tonyIt sounds to me like you are the person responsible for warming up the planet!
Posted By: GaryBIf so, then make sure the secondary pump is turned off during collection as the circulating losses often match the solar collection input.
Posted By: Nick ParsonsHang on - your HP is heating your *panels*??
Posted By: divergavIt's as if the hot water produced by the Heat pump goes up to the tubes, but heat from the tubes doesn't come down.This is not as silly as it sounds. The heat provided by the heat pump could be lost over night by thermosyphoning, where the warm water from your DHW tank rises up to the panels where it cools & drops back down to the tank again. This can be stopped by a correctly installed non-return valve.
Posted By: divergavEven if a valve or pump wasn't working surely the temp readout on the panel would be accurate wouldn't it?The temperature readout may be accurate, but if the temperature sensors are cross-wired or there's cool water circulating through the panel it won't get hot. Is there anywhere else the heat could be going? Is the system dedicated to DHW? Is there a heat dump radiator?