Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorgeorgiegirl
    • CommentTimeOct 3rd 2023 edited
     
    We live in a 1930s house in the South East. We installed 100mm EWI in 2019 and generally have a low heat demand, but unfortunately due to having an annexe with a shared meter I don't know what our kWh heat demand actually is.

    We have also installed a 6kW pv array with 5kW battery storage last winter. We are currently still on a fixed tariff that is about to end, but will then switch to either an ev or economy 7 tariff. We are also about to renovate our ground floor. The gas boiler will need to be moved, but I'm more inclined to ditch the gas and so am looking for an alternative to the combi boiler.

    I came across the McDonalds Electrastore thermal store and thought it sounded really interesting. It has 2 immersions at the bottom to heat from E7 or time of use tariffs and another immersion higher up to boost the top of the store during the summer for hot water requirements.

    I just wanted to run my thoughts past those who know better than me please. I'm thinking that during the summer a diverter could take excess from our PV array to heat the top of the store for evening showers. Central heating won't be required so the bottom immersions aren't needed. When its cold enough to switch the heating on the bottom immersions would be activated and heat the tank at the cheap rate. Does this sound like it could work? Alternatives that don't involve heat pumps? Thanks
    • CommentAuthortony
    • CommentTimeOct 3rd 2023
     
    It will work, yes but it might be expensive and you will almost certainly end up using peak rate electricity to heat your home in cold weather.

    Electricity is 100% efficient at heating, off peak can be 1/4 the price of peak rate electricity but there will be some losses from the store 30 to 50%

    A heat pump can be 350% efficient with no losses. What do you have against heat pumps?
    •  
      CommentAuthordjh
    • CommentTimeOct 4th 2023 edited
     
    Posted By: georgiegirldue to having an annexe with a shared meter I don't know what our kWh heat demand actually is.
    It would probably be fairly simple to have a sub-meter put in to measure the annex's consumption. Or even a CT clamped around the cable (Current Transformer) would give a good idea.

    I'm thinking that during the summer a diverter could take excess from our PV array to heat the top of the store for evening showers. Central heating won't be required so the bottom immersions aren't needed. When its cold enough to switch the heating on the bottom immersions would be activated and heat the tank at the cheap rate. Does this sound like it could work? Alternatives that don't involve heat pumps?
    We have a very similar arrangement. Our house is a passivhaus so has a low space heating demand met by direct electric heating. We heat our hot water using a Gledhill thermal store with two immersions. The bottom one is connected to a diverter that diverts spare energy from our 4 kW PV system. It is set to a high temperature to maximise storage capability. The top immersion is fed from the mains through a timeswitch and is set to a lower 60°C temperature. That provides enough hot water in the winter for our two showers a day plus all other domestic needs. It doesn't use any power in the summer because the water is already above 60°C because of the solar diversion.

    I haven't been able to justify the cost of installing and maintaining a heat pump yet, given our low heat demand. Losses from the thermal store in winter aren't really losses at all since they are picked up by our MVHR extract and recycled into the air supply, avoiding some of the space heating demand. During summer the losses are from free PV power and the heat is dumped by the MVHR summer bypass so it isn't a problem then either. WE use an E7 tariff at present.

    What is best for you will depend on exactly what your space and water heating demands are.
  1.  
    Posted By: georgiegirlAlternatives that don't involve heat pumps?


    Just to throw something else into the mix, we are all electric and passivhaus like djh above. However we are using a thermal battery to absorb our excess PV. Specifically SunAmp, though I think there may now be others available.

    This uses a phase-change salt material to store the heat which is more 'energy-dense' than water, so sits in a smaller footprint than the equivalent water tank would need to be.

    Generally it has been a mixed-bag for us. Being early adopters we bought direct from the manufacturer and thus have suffered both from a lack of post-sales customer support and the fact that one battery is, in retrospect, undersized and doesn't deliver enough hot water for our needs.

    Neither issue is something that would affect you necessarily, but it helps to be informed! Now we've had it for 5 years, my only other observation would be that it should work well with a PV battery because you can spread out the charging profile through the day.

    Generally the 'guilt-free' hot water in summer is a real benefit and I'm happy we went for this route rather than a direct electric 'zip' heater for example.
  2.  
    Posted By: tonyIt will work, yes but it might be expensive and you will almost certainly end up using peak rate electricity to heat your home in cold weather.

    Electricity is 100% efficient at heating, off peak can be 1/4 the price of peak rate electricity but there will be some losses from the store 30 to 50%

    A heat pump can be 350% efficient with no losses. What do you have against heat pumps?


    Thanks, nothing against heat pumps, but I understand they can't work with a thermal store and that's ideally what I want.
  3.  
    Posted By: djh
    Posted By: georgiegirldue to having an annexe with a shared meter I don't know what our kWh heat demand actually is.
    It would probably be fairly simple to have a sub-meter put in to measure the annex's consumption. Or even a CT clamped around the cable (Current Transformer) would give a good idea.

    I'm thinking that during the summer a diverter could take excess from our PV array to heat the top of the store for evening showers. Central heating won't be required so the bottom immersions aren't needed. When its cold enough to switch the heating on the bottom immersions would be activated and heat the tank at the cheap rate. Does this sound like it could work? Alternatives that don't involve heat pumps?
    We have a very similar arrangement. Our house is a passivhaus so has a low space heating demand met by direct electric heating. We heat our hot water using a Gledhill thermal store with two immersions. The bottom one is connected to a diverter that diverts spare energy from our 4 kW PV system. It is set to a high temperature to maximise storage capability. The top immersion is fed from the mains through a timeswitch and is set to a lower 60°C temperature. That provides enough hot water in the winter for our two showers a day plus all other domestic needs. It doesn't use any power in the summer because the water is already above 60°C because of the solar diversion.

    I haven't been able to justify the cost of installing and maintaining a heat pump yet, given our low heat demand. Losses from the thermal store in winter aren't really losses at all since they are picked up by our MVHR extract and recycled into the air supply, avoiding some of the space heating demand. During summer the losses are from free PV power and the heat is dumped by the MVHR summer bypass so it isn't a problem then either. WE use an E7 tariff at present.

    What is best for you will depend on exactly what your space and water heating demands are.


    Great to hear that you have a similar set up, but interesting that you have the immersions functioning they other way around. I've spoken to a couple of thermal store suppliers and they are suggesting that I will need a very large store in order to compensate for the store not being heated by a 24kw boiler. However, as we have also got approx 70m2 of underfloor heating being installed thatthe volume can be reduced as heat will be stored in the slab.
  4.  
    Posted By: Doubting_Thomas
    Posted By: georgiegirlAlternatives that don't involve heat pumps?


    Just to throw something else into the mix, we are all electric and passivhaus like djh above. However we are using a thermal battery to absorb our excess PV. Specifically SunAmp, though I think there may now be others available.

    This uses a phase-change salt material to store the heat which is more 'energy-dense' than water, so sits in a smaller footprint than the equivalent water tank would need to be.

    Generally it has been a mixed-bag for us. Being early adopters we bought direct from the manufacturer and thus have suffered both from a lack of post-sales customer support and the fact that one battery is, in retrospect, undersized and doesn't deliver enough hot water for our needs.

    Neither issue is something that would affect you necessarily, but it helps to be informed! Now we've had it for 5 years, my only other observation would be that it should work well with a PV battery because you can spread out the charging profile through the day.

    Generally the 'guilt-free' hot water in summer is a real benefit and I'm happy we went for this route rather than a direct electric 'zip' heater for example.


    I looked at the Sumamps,but they only do hot water and not heating. How do you provide heating?
  5.  
    Posted By: georgiegirlHow do you provide heating?


    Sorry, I hadn't picked that up from your first post. We're in a passivhaus so heating is minimal and provided by 2x 600W electric panel heaters.

    My understanding of the SunAmp is that it was designed as a 'drop-in' alternative to a hot water cylinder, so yes you'd need something else to do the 'boiler' part. This could be an ASHP, but I realise you're trying to avoid this route.

    **Edited to add, the SunAmps do have a heating element so you can run them as water heaters like an immersion tank, especially on an off-peak tariff. We actually do this each night on our smaller unit to ensure that we've got enough for showers in the morning.

    However, I'm not sure how efficient it would be to use it in this way for space-heating.
    •  
      CommentAuthordjh
    • CommentTimeOct 5th 2023 edited
     
    Posted By: georgiegirlThanks, nothing against heat pumps, but I understand they can't work with a thermal store and that's ideally what I want.
    I don't understand that. It sounds like nonsense. What's the supposed reason for that particular idea?

    Great to hear that you have a similar set up, but interesting that you have the immersions functioning they other way around. I've spoken to a couple of thermal store suppliers and they are suggesting that I will need a very large store in order to compensate for the store not being heated by a 24kw boiler. However, as we have also got approx 70m2 of underfloor heating being installed thatthe volume can be reduced as heat will be stored in the slab.
    Our thermal store is 250 L. That provides enough hot water for two or three days for the two of us from a single sunny day. It only supplies DHW, not space heating. What is 'a very large store'? And why does it need to be larger if you don't have a 24 kW boiler?

    Go back to basics. What is your heat loss and DHW consumption? Put in another meter and find out.
    • CommentAuthorborpin
    • CommentTimeOct 5th 2023
     
    Posted By: georgiegirlThanks, nothing against heat pumps, but I understand they can't work with a thermal store and that's ideally what I want.
    I'm inclined to think the opposite, but I seem to be in a minority.

    Key thing seems to be that the coil inside the tank that does the water heating, has to be large enough to heat the DHW without the tank itself being excessively hot.

    Other than that, and for wet heating systems, a TS seems to be an ideal solution as the flow return for the HP is then independent of the heat demand of the house, it is just to do with the heat demand of the TS. This should then give long runs for the HP.

    There does need to be good stratification and the ability to just heat the bottom of the tank so keeping the flow temps from the HP down at times.
    •  
      CommentAuthordjh
    • CommentTimeOct 5th 2023
     
    FWIW, our thermal store has an external PHE instead of an internal coil to heat the DHW, so it's simply a matter of ensuring the PHE is correctly rated (and easy to change if a larger one is needed later).
  6.  
    .
    What is 'a very large store'? And why does it need to be larger if you don't have a 24 kW boiler?

    Go back to basics. What is your heat loss and DHW consumption? Put in another meter and find out.


    I don't understand it enough hence why I am hear asking questions of those that know more than me.

    One of the chaps that I spoke to from a manufacturers said that with the immersion providing 3kw that it would take 8 times longer to heat the store compared to a 24kW boiler. At least that's how I understood what he was saying.

    Someone at a different company said that a 300l store would only be sufficient for a 2 bedroom flat.
  7.  
    I don't have time to put in another meter as building work is imminent.

    For the last 2 winters we have had 3 radiators heating the house, 2 on the ground floor and one in our bedroom. thermostat set at 20. The rear extension (kitchen) had no heating or insulation in the roof, fortunately there were double glazed doors between there and the living room. The roof will be insulated, the floor dug up and insulation under the new slab plus UFH as part of the building works.
  8.  
    Simplifying/generalising my comments below, as it takes a detailed conversation and background building data to design these systems properly, but maybe there'll be something useful for you...

    t's not "usual" to have a thermal store, as it's often a means to decouple when you can input energy from when you use that energy (or different types of energy inputs). An ASHP can pretty much run on demand, so "usually" you would not run it and store the heat, to be used later. People then conflate that, into stating that it cannot be done. I must be carrying out miracles, cause I've done it a number of times.

    You really need to have an idea of the heat loss for your home (in the post-refurb state) so you can understand if the rate of heat you can put in will match the rate of heat you are losing. That's a capacity/sizing/power question. That would determine the size of the thermal store, as you need to be able to store the heat when it's cheap, and release that over the expensive period. With Eco7, there's not that big a diff between night and day rate. Similarly with Eco10 (if you can get that). The flexible Octopus type tariffs can have quite low off peak rates, but you'd again need to run some numbers, as the onpeak tariffs are huge.

    Then you need to understand over 12 months, the quantity of energy (let's say in kWh) so you can decide if off-peak "direct" elect (immersion/panel heater) will be affordable when multiplied by the number of kWh of energy consumed.

    You also need to play in to all these figures, how PV and batteries can supplement. This is not NASA stuff, but it's not finger in the air stuff either.

    None of that is news to you I suspect, but my point is that rushing in to a decision, or asking a bunch of people who don't have the data to make an informed decision, may not deliver the optimal solution.

    I think I understand:
    - located SE England (likely rarely below 0oC and decent sunshine hours)
    - reasonable insulation
    - ground floor UFH
    - existing gas boiler to be relocated, so maybe get rid now, and use immersions for heating & DHW
    - have 6kW PV and 5kW batteries

    On the little info I have, (I design these systems), you might consider the following, if you do not gather/calc the heat loss info, or annual energy consumption data.

    1. instead of spending money on a thermal store, which I imagine would be £4k installed, add to your batteries. Store energy as elect in the battery, not as hot water made from elect. Import on a flexi tariff at the lowest times.
    2. use a small inline elect heater to heat water that would feed the UFH and the DHW cylinder (just like your gas boiler does at the moment). Maybe 3-4kW would suffice for a few £hundred (easy to upgrade if it's not enough, though if it's not big enough you're going to have hefty elect bills).
    - design for the installation of a small ASHP in the future (space for external unit, a small buffer tank internally, and ducts to allow the insulated pipes to run through your ext wall to get from the ASHP ext unit to the buffer tank location...BUT do not install the ASHP

    That should minimise your spend now, allow usage of lower rate elect times by providing storage of energy, allow you to test out the direct electric option, and if it proves very costly to run, you could flip to an ASHP very easily. You'll also know what size of ASHP would be required, as you'll have lived with the heating system.
  9.  
    Was going to say some stuff, but Green Paddy put it very much better!

    No point metering your existing consumption patterns if you're just about to insulate.

    You can estimate your future consumption by doing calculations of more or less complexity, looking at the floor area and insulation thickness, an installer should be doing that rather than saying 'this is ok for a 2-bed' as it really depends on your insulation.

    As a shortcut (with risk of being too short) here is a cheat sheet
    https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/

    Let's say a house needs 50W/m² on the coldest day and is 100 m² floor area (substitute your own details here) then it would need 50x100= 5000W = 5kW of heating (about 3 big radiators).

    That's 5x24 = 120kWh each day - costs £40 on normal tariffs but maybe £20 off-peak, ouch! Save two-thirds off that cost with a heat pump.

    If they wanted to store a whole day of heat in a TS, they would spend say 6 hours off-peak heating it up and 18 hours drawing from it, so store say 5kWx18h= 90 kWh

    To store a kWh in water that is heated up to 80⁰ and then used in rads/UFH at 40⁰, needs 3600/4.2 /(80-40)= 20 litres of TS

    So to store the 90 kWh would take 90 X 20 = 1800 litres. That's a really big TS.

    That's why TS are often used for hot tap water, but less often for central heating.

    But all is not lost!

    - If the house is really well insulated, and smaller, it needs less heat
    - not every day gets that cold, the TS could be made big enough for autumnal weather and be supplemented on-peak during midwinter
    - some tariffs have several off peak periods each day, eg cheaper in the afternoon as well as overnight. So the store could just hold half a day's heat, and be reheated twice a day.



    To charge up the TS to 80⁰ is too hot for a heatpump to run at max efficiency, it would be much more efficient running all day, directly to the UFH at 40⁰. That's why people say not to run a TS with a heatpump. And they wouldn't need such a big heatpump if it can run steadily all day, instead of doing the same work in fewer hours.

    However people happily heat hot tap water cylinders to 50⁰-60⁰ with heatpumps and a TS is no different. If the electricity is much cheaper off-peak then they might not care that the heatpump is less efficient. Even if the heatpump runs at low efficiency, it's still more efficient than an immersion heater.


    To import the whole day's 120kWh of heat during a 6-hour off peak period, would take 120/6 = 20 kW of immersion heaters, that's a lot and the house mains supply might be a limitation. A heatpump would draw much less electricity.
    •  
      CommentAuthordjh
    • CommentTimeOct 6th 2023
     
    Posted By: georgiegirlI don't have time to put in another meter as building work is imminent.
    Alarm bells are ringing. Doing building work when you don't know basic details nor exactly what you are aiming for is a recipe for disaster. Wasted money and poor results perhaps.

    I agree with what Green Paddy said.

    Posted By: WillInAberdeenNo point metering your existing consumption patterns if you're just about to insulate.
    There is a point in being able to monitor energy consumption going forward, and there is a point in measuring current consumption so as to be able to calculate the difference from a baseline. Starting from data is better than starting from theoretical calculations.

    Installing a meter is something an electrician can do in a hour or so. Installing a CT clamp is a DIY job.
  10.  
    Fair enough, I'll rephrase:
    "No point designing your future heating system based on your existing consumption patterns if you're just about to insulate."
Add your comments

    Username Password
  • Format comments as
 
   
The Ecobuilding Buzz
Site Map    |   Home    |   View Cart    |   Pressroom   |   Business   |   Links   
Logout    

© Green Building Press