Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorjms452
    • CommentTimeMar 27th 2021
     
    Our current loft mounted MVHR unit screws onto the ceiling joists and is buried under loft insulation keeping it nicely insulated.

    http://www.nuaire.info/IandM/671438.pdf

    However, it is 10 years old, the fans were replaced under warranty after about 4 years when the engineer told us that they no longer use that type of fan in the newer units due to poor lifetime. One of the fans is starting to go again so I'm looking at options. It is also rather primitive in that you need to take it apart to change the filters which is a bit of a pain.

    Most of the current units (e.g. Vent-Axia 438222 Sentinel Kinetic B) have neat easy change filters and talk about loft mounting but they are effectively wall mount units and our loft is 'cold'. As the units are not particularly well insulated I'm contemplating building a PIR box around such a unit in the loft but this will make access a pain.

    Any thoughts - common sense tells me there must be a decent accessible + insulated MVHR out there but I'm not seeing it.
  1.  
    Are the new type fans compatible (or adaptable) with the old units If so it may be easier and cheaper to put new style fans in your unit.
    • CommentAuthorrevor
    • CommentTimeMar 27th 2021
     
    I have a Titon unit which is basically an engineered polystyrene box housing all the gubbins, so is insulated and quiet except on boost. It is quite old now and may no longer be available. But have look see.
    Ours is wall mounted but it is light enough and could easily be hung on a frame. The condensate drain is on the bottom so could not be placed on any surface.You have to take the front off to change the filters 5 min job once a year. It is in a plant/utility room.
    •  
      CommentAuthordjh
    • CommentTimeMar 27th 2021
     
    Posted By: jms452I'm contemplating building a PIR box around such a unit in the loft but this will make access a pain

    Can you not build a box where the 'lid' of the box is the 'front' of the MVHR that you need to access for the filters? Then unclipping a couple of hook and eye fasteners and lifting the lid out of the way wouldn't take long. Or is your situation more complicated? I'd have expected aligning the new ducts with the old ducts might be more complicated.
    • CommentAuthorjms452
    • CommentTimeMar 27th 2021
     
    Posted By: Peter_in_HungaryAre the new type fans compatible (or adaptable) with the old units If so it may be easier and cheaper to put new style fans in your unit.


    I'm time poor these days and trying to avoid having to build my own unit, would also be nice to be able to change the filters cleanly and easily.

    Posted By: revorI have a Titon unit which is basically an engineered polystyrene box housing all the gubbins, so is insulated and quiet except on boost. It is quite old now and may no longer be available. But have look see.


    They have pretty good specs but I wouldn't be happy with 1cm on polystyrene anywhere else on the house.

    Posted By: djhCan you not build a box where the 'lid' of the box is the 'front' of the MVHR that you need to access for the filters? Then unclipping a couple of hook and eye fasteners and lifting the lid out of the way wouldn't take long. Or is your situation more complicated?


    Getting a nice seal is the bit that becomes involved.


    I can do it all but I'm getting lazy and was hoping a '2 day' job rather than a 'week job'
    •  
      CommentAuthordjh
    • CommentTimeMar 27th 2021
     
    Posted By: jms452Getting a nice seal is the bit that becomes involved.

    Ah, you're more of a perfectionist than me. Stick a bunch of window draught strip around the edge, would do it for me. It doesn't have to be perfect, I don't think. The units should be plausibly well-insulated anyway.
    • CommentAuthortony
    • CommentTimeMar 27th 2021
     
    The unit will be half warm, house air temperature and half cold (outdoor temperature) less fan heat losses

    Complex problem
    • CommentAuthorjms452
    • CommentTimeMar 28th 2021
     
    @revor - How would you report on the Titon?
    How long have you ran it for?
    Breakages & spares?

    cheers

    J
    •  
      CommentAuthordjh
    • CommentTimeMar 28th 2021
     
    Posted By: tonyThe unit will be half warm, house air temperature and half cold (outdoor temperature) less fan heat losses

    That's why
    Posted By: djhThe units should be plausibly well-insulated anyway.
    :bigsmile:
    • CommentAuthoran02ew
    • CommentTimeApr 2nd 2021
     
    IMO they just shouldn’t be mounted in an uninsulated space. But as you have already crossed that bridge then a purpose built celotex (or other) box would be a must. Shouldn't take long and you could foam any gaps. Laminating up the layers off-setting joins to really get a good seal. There isn’t any unit on the market that will copy with subzero temps without losing all its saved energy or worse becoming a dripping mess of condensation.
    • CommentAuthorrevor
    • CommentTimeApr 3rd 2021
     
    @jms452. I have had my unit since 2012 but was not commissioned for some time as we needed it for positioning duct runs which we were doing during the build and house is still not fully balanced. We do not use it all of the time. It is on if we are showering (on boost) cooking (we have a recirculating extractor the MHVR then picks up the exhaust in the kitchen). Generally do not use at night in the winter as not much point drawing in cold air but it is used at night if the house got a bit too warm during the day. It is a fairly large property and only 2 of us so we do not have issues with condensation that would need us to run unit full time. So having set out the way it is used to put usage into context we have not had any issues with it at all (hope not tempting fate). It was easy to set up clear instructions. Filters are readily available from Titon I did look for an alternative supply but could not find a supplier of the size required. Last time I bought a box of 12 sets I think, they come with a time in use sticker which helps keep track of when time to change. I usually change them every 12 months.
    •  
      CommentAuthordjh
    • CommentTimeApr 3rd 2021
     
    Posted By: an02ewIMO they just shouldn’t be mounted in an uninsulated space. But as you have already crossed that bridge then a purpose built celotex (or other) box would be a must. Shouldn't take long and you could foam any gaps. Laminating up the layers off-setting joins to really get a good seal. There isn’t any unit on the market that will copy with subzero temps without losing all its saved energy or worse becoming a dripping mess of condensation.

    Do you have any references to back up your opinion?

    As Tony says, an MVHR is full of air half at room temperature and half at outside temperature. The unit itself is insulated to prevent heat loss or gain in either circumstance, and whichever ducts are in the 'wrong' zone clearly need to be well insulated. But beyond that, and ease of access to change filters etc, I don't know of any reason it can't be mounted somewhere colder than normal. Note that we are talking about internal spaces such as lofts or garages or externally-accessed cupboards and these will not normally freeze.

    GBS seems to agree: https://www.greenbuildingstore.co.uk/mvhr-dos-donts-where-to-locate-mvhr-unit/
    • CommentAuthoran02ew
    • CommentTimeApr 3rd 2021
     
    I’m not surprised GBS advocate the use in uninsulated areas, it’s not good business to advise against install in cold zones.

    As for installation in cold areas, so long as ducting and distributing boxes are well and meticulously insulated and the unit is has additional insulation too then you should be ok. But I have seen installs were a bit of loft roll is tucked haphazardly around duct and nothing around distribution boxes. Turning it into MVNHR( no heat recovery) which is just a waste on money. And seen condensation on the external surface of the fan unit.

    Unrelated, I’ve also seen the intake vent completely frozen solid. Cold foggy conditions and a modern stainless grill type vent, resulted in the incoming moist air condensating on the cold metal grill and freezing over completely.
    •  
      CommentAuthordjh
    • CommentTimeApr 4th 2021
     
    Posted By: an02ewAs for installation in cold areas, so long as ducting and distributing boxes are well and meticulously insulated and the unit is has additional insulation too then you should be ok. But I have seen installs were a bit of loft roll is tucked haphazardly around duct and nothing around distribution boxes. Turning it into MVNHR( no heat recovery) which is just a waste on money. And seen condensation on the external surface of the fan unit.

    That's all true but applies equally to the intake and exhaust ducts when the unit is installed in a warm area. In fact more so, since they're liable to condensation on their surface. But again, why do you think the situation is any different for the unit itself whether it is in a warm or cold area?
  2.  
    As regards GBS and MVHR I can only confirm that, on the job I was involved with, they were very clear that the unit should be within the house itself (we had originally intended to build it an insulated 'house' within the cold loft). And I don't think the link implies wholehearted support for installation outside the heated envelope:


    ''....Despite our reservations, in some cases we have sited MVHR units in lofts, commonly in retrofits and smaller projects.''
    • CommentAuthoran02ew
    • CommentTimeApr 4th 2021
     
    <blockquote><cite>Posted By: djh</cite>But again, why do you think the situation is any different for the unit itself whether it is in a warm or cold area?</blockquote>

    If your looking for your MVHR to recover anywhere near its quoted efficiency figures then it’s needs to be within the thermal envelope of the building. That includes the ducting and distributions. Forget the summer bypass when you’ve got the system in a 40+ degree loft with a bit loft roll stuff around it.

    If your spending 2k plus on MVHR and it’s in the loft then spend another £500 and seriously insulate fastidiously otherwise your wasting the original 2k
    •  
      CommentAuthordjh
    • CommentTimeApr 4th 2021
     
    Yes you can repeat your assertion as much as you like, but please show the evidence. You may well be right but there's no particular reason I should believe you unless you offer some backup.

    And again, specifically the MVHR unit. The ducts and distribution boxes etc are obvious.
    • CommentAuthoran02ew
    • CommentTimeApr 4th 2021
     
    Believe what you like. And mount you MVHR were you like, it’s your money you can poke it down whatever drain you like too.
    Ive commissioned plenty of systems and I’ve seen some shocking installs and condensation on the outer casing.
    • CommentAuthoran02ew
    • CommentTimeApr 4th 2021
     
    All I’m saying is a devise that tenuously removes heat from outgoing air needs all the help it can get. :sad:
    • CommentAuthorjms452
    • CommentTimeApr 4th 2021 edited
     
    Thanks for the thoughts all.

    Unit is in the loft and the last one was insulated with 50mm PIR (plus token insulation of the unit). All the warm duct runs are under at least 200mm of loft insulation.

    As Tony says half is warm and half cold - In that case I might get improved performance if insulation is closely pressed onto the unit?

    Andrew I'd much prefer to have it internally and appreciate your experience on this - looks like some meticulous detailing is in order.

    [edited for typo]